billyO

Hello all.  I'm upgrading my forge with a PID controller and 2 different SSR set-ups have been suggested:
a) 25A SSR (SRDA25) with a heat sink (HS25) or
b) 40A SSR (SRDA40) without a heat sink. 
Option (b) would be a little cheaper and require less room, but I'm more interested in safety and longevity of the components. 
Thank you.
as always
peace and love
billyO

billyO

as always
peace and love
billyO

Kkane

Option b is incorrect. If your load/heating element is over 6A, you have to use a heat sink together with your SSR. If your load is within 25A, you can use 25A, or 40A SSR for better lifetime. But 25A heat sink is needed anyway.