Updates:

Click here to visit our store! https://www.auberins.com

Programs stuck in Hold

Started by EK Blade Arts, March 16, 2024, 10:30:22 AM

Previous topic - Next topic

EK Blade Arts

I have a 2352p on a heat treating oven
My program is flashing hold no matter how i modify the program parameters?
What can i do do reset and get put of HOLD
Many Thanks

EK Blade Arts

My program is
CO 1 500
TO 1 10
CO 2 500
TO 2 15
CO 3 500
TO 3 -121

Parameters
Alm1 1900
Alm2 40
Hy1 1
Hy2 1
Hy 0.3
At 0
I 1000
P 500
D 120
t 2
Sn 0
Dp 0
P-sl 100
P-sh 2500
Pb 0.0
Op-a 0
Outl O
Outh 100
Al-p 17
Cool 10
Hddr 1
Baud 4800
File 0
A-m 2
Lock 808
Ep-1 - Ep 8 none

Kkane

Hy1 1
Hy2 1
Hy 0.3

So you are using safety start. When you cold start the setup, your timer will be on hold until your reading temp gets to 500.

You can set Hy1 and Hy2 back to the default (9999) to turn off safety start. So you can run the program normally.

For safety start, please see page 7, middle section on the right of its manual.

Also, you set AT to 0 and you are using on/off mode.

P-SL please confirm 100 or -100. It should be -100.